Hi all
I've a 3 year old Ravenheat HE85T combi boiler which has had new dry clip on CH and wet pocket type DHW therminsters, diverter valve, microswitch and fan PCB in the past.
This morning the boiler starter fine in the morning at 6:30 am and then at around 7 am, when DHW was started, the boiler stopped with RED overheat light ON. the fan was still running.
I checked the pressure which was slightly less than 1 bar, so I topped it up to 1.5 bar but it was of no use.
I've also checked the condensing pipe for any blockage and there was none. I've infact left it open all day to get rid of any moisture.
But there is still no DHW or CH.
I've reset it so many times now (power reset) but every time I start up the fan starts but I can't hear the pump starting (sound of a second motor which is a little bit more noisy and sounds more powerful than the fan one). The pump does not start for DHW or CH. RED light comes after some time.
I've checked the resistance of thermisters and they are fine, even put new ones on and still the problem is there/ no effect.
I've cheked the main PCB/ ignition board FUSE and that is intact. The microswitch and the knobs for DHW and CH (winter/summer mode) are also working along with the timer.
I've checked the power supply to the water pump after opening its microswitch and its 240V there, I've wiggled the capacitor on pump and some wires on PCB (reconnected all connectors) but all invain.
Is it safe to assume now that my water pump is gone and I need to order a new one (0009CIR01011/1)? Are there any more tests that I should do now?
I presume pump is an easy thing to replace or should I be careful about something? Do I need any new washers while replacing the pump?
Sorry for the long post and many thanks in advance to all the kind souls for their helpful replies..
Kunal
I've a 3 year old Ravenheat HE85T combi boiler which has had new dry clip on CH and wet pocket type DHW therminsters, diverter valve, microswitch and fan PCB in the past.
This morning the boiler starter fine in the morning at 6:30 am and then at around 7 am, when DHW was started, the boiler stopped with RED overheat light ON. the fan was still running.
I checked the pressure which was slightly less than 1 bar, so I topped it up to 1.5 bar but it was of no use.
I've also checked the condensing pipe for any blockage and there was none. I've infact left it open all day to get rid of any moisture.
But there is still no DHW or CH.
I've reset it so many times now (power reset) but every time I start up the fan starts but I can't hear the pump starting (sound of a second motor which is a little bit more noisy and sounds more powerful than the fan one). The pump does not start for DHW or CH. RED light comes after some time.
I've checked the resistance of thermisters and they are fine, even put new ones on and still the problem is there/ no effect.
I've cheked the main PCB/ ignition board FUSE and that is intact. The microswitch and the knobs for DHW and CH (winter/summer mode) are also working along with the timer.
I've checked the power supply to the water pump after opening its microswitch and its 240V there, I've wiggled the capacitor on pump and some wires on PCB (reconnected all connectors) but all invain.
Is it safe to assume now that my water pump is gone and I need to order a new one (0009CIR01011/1)? Are there any more tests that I should do now?
I presume pump is an easy thing to replace or should I be careful about something? Do I need any new washers while replacing the pump?
Sorry for the long post and many thanks in advance to all the kind souls for their helpful replies..
Kunal