Please, I know these boilers get a load of stick but I'm stuck with one and could really do with some help!
I woke this morning to find my boiler ignition failure light blinking. Turning the power off and on didn't fix it and the pressure in the system is fine at 1 bar.
The boiler currently does the following:
- DHW is called for.
- Water pump runs.
- Main PCB fan relay clicks on and off about 10 times (one every 2 seconds or so).
- Water pump stops 20s later.
Now this would immediately make me think that the fan relay was broken but... when I remove a wire from either the overheat stat, low water pressure switch or flow switch, this happens:
- DHW is called for.
- Water pump runs.
- Fan runs.
- Fan and water pump stop 20s later.
- Red ignition failure light blinking.
The process of operation on this boiler is meant to be Pump, Sensors, then fan. So I'm not sure how removing one of three random sensor wires allows it to continue.
This has been exhausting checking that every sensor I can get my multi meter into. I'm only a little unsure about the pot values. I got about 17Kohm on both the CH and DHW pots. The overheat stat was shorted (not sure if this is right?).
I've also replaced the fan control board with a spare I repaired a while back (I tested it after repair and it worked back then).
Please, if there is anything I've missed, lemme know!! It horrible sat here in the cold
Thanks guys,
Andy
I woke this morning to find my boiler ignition failure light blinking. Turning the power off and on didn't fix it and the pressure in the system is fine at 1 bar.
The boiler currently does the following:
- DHW is called for.
- Water pump runs.
- Main PCB fan relay clicks on and off about 10 times (one every 2 seconds or so).
- Water pump stops 20s later.
Now this would immediately make me think that the fan relay was broken but... when I remove a wire from either the overheat stat, low water pressure switch or flow switch, this happens:
- DHW is called for.
- Water pump runs.
- Fan runs.
- Fan and water pump stop 20s later.
- Red ignition failure light blinking.
The process of operation on this boiler is meant to be Pump, Sensors, then fan. So I'm not sure how removing one of three random sensor wires allows it to continue.
This has been exhausting checking that every sensor I can get my multi meter into. I'm only a little unsure about the pot values. I got about 17Kohm on both the CH and DHW pots. The overheat stat was shorted (not sure if this is right?).
I've also replaced the fan control board with a spare I repaired a while back (I tested it after repair and it worked back then).
Please, if there is anything I've missed, lemme know!! It horrible sat here in the cold
Thanks guys,
Andy