Hi,
Looking for a bit of advice with the Ravenheat LS100. Over the recent months I have replaced just about every part on this thing and am still having difficulty although it was running perfectly at one point.
Situation is, I have a problem with the boiler overheating when the water flow-rate and demand is high.
If I open the hot water tap 3/4 of the way, the modureg kicks in, and I see the gas pressure fluctuate up and down and the boiler maintains temperature of the water.
If I open the tap fully (equivalent flow as if taking a shower). I see the modureg go up to 16mbar which is wide-open as it attempts to heat the water. About 30 seconds later I then hear the water begin gurgling as it sounds like it begins to boil and overheat, and the system shuts down, and then relights. This is resulting in hot&cold showers. To fix, I simply turn down the flow rate, and I get weaker albeit hot regulated showers.
I've tested the thermistor and it goes down to 4kOhms from 20kOhms. So looks as though it's working. I'm of the opinion that 4k is a good reading for a hot system, but should it be reading lower? Strikes me that it's unlikely to be the thermistor if its regulating the temperature at lower flow.
I suspect I have an airlock or waterlock but not sure where, there's a red bleed valve for the CH but unsure why its overheating. Clearly the thermistor is telling the system to keep the modureg wide open, so my guess is water is boiling near the overheat thermostat, any thoughts?
Looking for a bit of advice with the Ravenheat LS100. Over the recent months I have replaced just about every part on this thing and am still having difficulty although it was running perfectly at one point.
Situation is, I have a problem with the boiler overheating when the water flow-rate and demand is high.
If I open the hot water tap 3/4 of the way, the modureg kicks in, and I see the gas pressure fluctuate up and down and the boiler maintains temperature of the water.
If I open the tap fully (equivalent flow as if taking a shower). I see the modureg go up to 16mbar which is wide-open as it attempts to heat the water. About 30 seconds later I then hear the water begin gurgling as it sounds like it begins to boil and overheat, and the system shuts down, and then relights. This is resulting in hot&cold showers. To fix, I simply turn down the flow rate, and I get weaker albeit hot regulated showers.
I've tested the thermistor and it goes down to 4kOhms from 20kOhms. So looks as though it's working. I'm of the opinion that 4k is a good reading for a hot system, but should it be reading lower? Strikes me that it's unlikely to be the thermistor if its regulating the temperature at lower flow.
I suspect I have an airlock or waterlock but not sure where, there's a red bleed valve for the CH but unsure why its overheating. Clearly the thermistor is telling the system to keep the modureg wide open, so my guess is water is boiling near the overheat thermostat, any thoughts?