I hope someone can help me diagnose this problem.
Symptoms
The DHW temperature never gets hot enough for the DHW stat to switch the burner from high to low. Even at low flow rates it never gets above 55C at the tap.
The main burner cuts out (leaving just the pilot) until temperature gets down to about 30C at the tap and it then fires up again until approx 55C.
Occasionally after drawing hot water the pilot light goes out.
Central heating works fine.
What I have tried so far.
1 Cleaned pilot burner jet and slightly increased gas to pilot. - Pilot still cuts out occasionally.
2 Replaced thermocouple and overheat stat (single replacement part). Pilot now cuts out only very occasionally.
3 Temporarily bypassed High Limit stat - DHW now gets hotter but overheat stat trips regularly as expected. Removed bypass.
4 Replaced High Limit stat - No improvement
5 Checked Automatic Air Valve causing it to leak water. Would not re-seal. Replaced with new valve.
6 Checked diverter valve. Operates to spec at between 2.5 and 3 litres per minute. Suspected may be partially blocked. Dismantled valve-end, removed a bit of debris and cleaned but no significant blockage. Reassembled. - No improvement.
7 Checked pump is running and in correct direction.
8 Fan runs at Hi and Lo speed as expected.
Conclusion
Either two faulty Hi Limit stats - What temperature should this open at? - I guess 85-90C. Can possibly test this with a clamp on pipe thermometer. (unfortunately the temperature gauge on the boiler has not worked for years)
OR Something is preventing adequate heat transfer from the primary CH water to the DHW circuit in the heat exchanger. We are in a soft water area so scaling is unlikely. Is it worth removing the heat exchanger and flushing through using a hose pipe?
I would be grateful if anyone could answer my couple of questions or suggest any other ideas.
Other forum users appear to have had similar problems, on other boiler types as well, but I cannot find any conclusive answers to say what solved the problem.
Many thanks in anticipation.
Symptoms