I think I may have finally beaten this thing into submission.
(Double burner, soft start Nu Way MX499k).
As the thing would go to frequent lockout, this was due to the initial start up pump pressure being as low as 60 psi due to a faulty bypass valve in the manifold that is pressurised by the pump up to 145 psi. The fuel couldn't atomise hence no ignition and lockout. Cleaning the hidden bypass allowed 100 psi initially so the flame could establish, and it would switch to 145 psi after 20 sec.
The Rayburn needing to be reset due to overheating was due to the water circulating pump overrun stat not working...I found a replacement that keeps the pump on once the boiler temp reached 65 deg, and stopped the pump when it came back down to 62 deg.
The replacement ST6400c programmer works brilliantly...!
If the thing doesn't start tomorrow morning I shall be found hanging from a nearby tree...I hate this thing with a vengance!
John
(Double burner, soft start Nu Way MX499k).
As the thing would go to frequent lockout, this was due to the initial start up pump pressure being as low as 60 psi due to a faulty bypass valve in the manifold that is pressurised by the pump up to 145 psi. The fuel couldn't atomise hence no ignition and lockout. Cleaning the hidden bypass allowed 100 psi initially so the flame could establish, and it would switch to 145 psi after 20 sec.
The Rayburn needing to be reset due to overheating was due to the water circulating pump overrun stat not working...I found a replacement that keeps the pump on once the boiler temp reached 65 deg, and stopped the pump when it came back down to 62 deg.
The replacement ST6400c programmer works brilliantly...!
If the thing doesn't start tomorrow morning I shall be found hanging from a nearby tree...I hate this thing with a vengance!
John