Here's the situation: I have (had) upstairs and downstairs lighting on separate circuits with 6A/30mA RCBOs. When I turned on the landing light (which is wired into the downstairs circuit) from ether hallway or landing switch, the downstairs RCBO trips. It also trips if I turn on the kitchen light (which is not dual switched), which (surely not by coincidence) runs through the same triple switch wall switch (hall light, landing light and kitchen light... don't ask - I just moved here, I didn't wire it).
OK... shared neutrals and all that, so I connected both circuits to the same RCBO. It still trips on the kitchen and landing lights if bulbs are fitted.
The RCBO does not trip if I take the bulbs out of the fitting, but does if I replace the LED bulbs for a filament, so it's not LED driver inrush (not that I thought it would be).
I tested the circuit's insulation and got 68 Mohm between earth and line/neutral shorted, and over 600 Mohm line to neutral. That was with the switches on but no bulbs in. So nothing to see there. I've checked the wiring in the switch and light fittings, all seems as it should. I haven't pulled up the floor boards yet.
Any hints what to look for?
OK... shared neutrals and all that, so I connected both circuits to the same RCBO. It still trips on the kitchen and landing lights if bulbs are fitted.
The RCBO does not trip if I take the bulbs out of the fitting, but does if I replace the LED bulbs for a filament, so it's not LED driver inrush (not that I thought it would be).
I tested the circuit's insulation and got 68 Mohm between earth and line/neutral shorted, and over 600 Mohm line to neutral. That was with the switches on but no bulbs in. So nothing to see there. I've checked the wiring in the switch and light fittings, all seems as it should. I haven't pulled up the floor boards yet.
Any hints what to look for?