RCBO
26 Jul 2011
Sussex
Hello all
I have an MK Sentry CU and was chatting to a friend who said I should have a 6amp RCBO fitted instead of the 6amp RCD I already have for my kitchen lighting curcuit. (The CU is situated inside a cupboard in the kitchen). Any ideas why I would need to change it?
He probably meant you should have a 6 amp RCBO in place of the existing MCB I have never seen a 6 amp RCD
Or did he mean your sockets needed an RCBO ?
Does your CU have an RCD ? If you are not sure then an RCD is most often a switch with a test button. Will be labelled 30 mA
I have never seen a 6A RCD. So please start again.
MCB - detects current and opens if it exceeds the thermal limit for a long time or magnetic limit immediately.
RCD - detects leakage current and trips if too much leaks to earth.
RCBO - Combines both.
Bernard & Eric
Many thanks for your replies.
Right..... I think I've got my facts straight now so I'll start again!
I've got an MK sentry CU which is split.
From left to right I've got the main switch which is red and marked 100A
Then I've got.....
1. B40 MCB (Cooker)
2. 6A MCB (Kit lighting)
3. B6 MCB (Lights FF)
4. B6 MCB (Lights GF)
5. B16 MCB (Spare)
6. B40 MCB (Induction hob)
Then I've got a blank plate followed by an 80A RCD with test button followed by from left..........
7. B32 (Kit Sockets on island)
8. B32 (GF Ring) plus spur off to garden shed.
9. B32 (FF Ring)
10. B32 (Kitchen Ring)
11. B16 (Patio Lighting)
The person I was speaking to siad I should change MCB No2 from 6A MCB to a 6A RCBO. Any ideas as to if this is neccassary?
Sorry about the first post, got my wires crossed between RCD's and MCB's!
Any advice appreciated
No it is not necessary unless you have any work done on that lighting circuit involving burying cables at a depth less than 50mm.
An RCBO would prevent/reduce a shock you got while changing light bulbs if you left the switch on etc....
Isn't it a worry that the cooker/hob are not RCD protected? but I guess it would have overloaded the RCD.
The ideal solution would be to replace everything with RCBO's.... or replace the board with a split RCD one, and then re-arrange the circuits to protect at least 1 lighting circuit from each RCD
Why carry out un-necessary work?
Maximum safety I suppose......
Plus the inconvenience in the case of a fault on the RCD side of this board would warrant it being improved in some way.
9. B32 (FF Ring)
A waterlogged patio light or leak down at the shed could be a bit of a nightmare with all of these sockets on the same RCD, and I wonder what rating it is?
Only if the cooker isolators incorporate socket outlets, otherwise its no issue at all
Assuming the CPC is terminated correctly. I can't think of many reasons at all why something would not be better protected by an RCD