RCD protected ring main

Joined
13 Feb 2005
Messages
249
Reaction score
1
Country
United Kingdom
Hi,

I am going to get an electrician to install the thermostat for my electric underfloor heating in my ensuite. I think the requirement is that the thermostat should be connected via a RCD fused spur, but a normal FCU can be used if the ringmain is protected by an RCD. My main fuse box is protected by an RCD for all my ringmains, does the meet the requirement or does there have to be a separate RCd for each individual ringmain.

thanks for any advice
 
Sponsored Links
Aslong as there is an RCD somewhere in the circuit, that is sufficient.

What you have sounds OK to me.
 
Thanks that great no need for an RCBO or a RCD FCU then, that saves some expense and also the fact that RCD FCU's are pretty ugly and it would have to be situated in my bedroom.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top