Whilst adding a small CU to a job today (to stop the garden lighting tripping the whole house) I ran into an issue with testing the rcd.
The Ze of the house (TT installation - quite a lot of them round here) was rather high at 200 Ohm but since the main CU had a 30ma main incomer could be considered compliant.
The problem came when testing the 30ma RCD in the new CU (Fed via henley block from the meter tails).
It passed the usual tests at 1/2I & 1I, but when it came to the 5I test my Megger MFT1552 would not test, because it detected the protective conductor voltage rising about 50V.
Note that it was the 50V limit that was stopping it, rather then the >40ms that I might have expected.
Since the RCD tripped at I in 33ms or so, I had no reason to suspect a dodgy rcd, but it appears that the poor earth was causing it to reach the limit and abort the test.
In fact there was an earth problem in the lighting circuit, which I will be returning to fix, but am I missing something here? I got the same results testing directly at the CU, where the Zs was 200 or less.
It appears from my reading that the 50V limit cannot be turned off on the Megger, although it seems that the regs only see it as an issue AFTER the 40ms time has expired?
Has anyone run into this before and found a work around, or is it a 'feature' of my Megger that I may run in to again.
Its late, but quick calcs suggest that an earth of > (50V / (5*150ma)) = 333 Ohm would always give this problem, and yet with rcds an earth of that value could still be considered compliant.
I realise that ideally fitting a new earth rod would be the answer, but since this job was just moving the garden lighting circuit to a separate rcd and not altering the existing setup the client may well not be prepared to consider if what is there is technically 'compliant'.
Any views welcome, and if I've missed something stupid I claim the late hour as an excuse
Gavin
The Ze of the house (TT installation - quite a lot of them round here) was rather high at 200 Ohm but since the main CU had a 30ma main incomer could be considered compliant.
The problem came when testing the 30ma RCD in the new CU (Fed via henley block from the meter tails).
It passed the usual tests at 1/2I & 1I, but when it came to the 5I test my Megger MFT1552 would not test, because it detected the protective conductor voltage rising about 50V.
Note that it was the 50V limit that was stopping it, rather then the >40ms that I might have expected.
Since the RCD tripped at I in 33ms or so, I had no reason to suspect a dodgy rcd, but it appears that the poor earth was causing it to reach the limit and abort the test.
In fact there was an earth problem in the lighting circuit, which I will be returning to fix, but am I missing something here? I got the same results testing directly at the CU, where the Zs was 200 or less.
It appears from my reading that the 50V limit cannot be turned off on the Megger, although it seems that the regs only see it as an issue AFTER the 40ms time has expired?
Has anyone run into this before and found a work around, or is it a 'feature' of my Megger that I may run in to again.
Its late, but quick calcs suggest that an earth of > (50V / (5*150ma)) = 333 Ohm would always give this problem, and yet with rcds an earth of that value could still be considered compliant.
I realise that ideally fitting a new earth rod would be the answer, but since this job was just moving the garden lighting circuit to a separate rcd and not altering the existing setup the client may well not be prepared to consider if what is there is technically 'compliant'.
Any views welcome, and if I've missed something stupid I claim the late hour as an excuse
Gavin