Apologies in advance for the lengthy post, and many thanks to those who make it to the end and provide me with an answer
While studying for my 2382-12 exam, I encountered the following question:
I believe the correct answer is C?
My understanding of the correct test procedure is this:
1) Test at 0.5 x In - RCD shouldn't trip
2) Test at 1 x In - RCD should trip within 200ms
3) Test at 5 x In - RCD should trip within 40ms
4) Check operation via Test button
Upon researching this question further, I find that Guidance Note 3 suggests the 5 x In test is only necessary on RCDs upto 30mA. However I'm struggling to find reference to this in the regulations - I see that 415.1 states that where a 30mA RCD is used for additional protection, it should trip within 40ms at 5 x In - does the fact this isn't stated for other scenarios or other uses of RCDs mean that those other scenarios don't require such testing? (Me being me is likely to test all RCDs as such anyway just for completeness and peace of mind)
Secondly, where in the regulations is it stipulated (or implied or calculated) that the RCD shouldn't trip at 0.5 x In, and that this should be tested?
While studying for my 2382-12 exam, I encountered the following question:
When testing a 100mA RCD the maximum test current applied via the test instrument will be
A. 3 x In
B. 5 x In
C. 1 x In
D. 1.5 x In
I believe the correct answer is C?
My understanding of the correct test procedure is this:
1) Test at 0.5 x In - RCD shouldn't trip
2) Test at 1 x In - RCD should trip within 200ms
3) Test at 5 x In - RCD should trip within 40ms
4) Check operation via Test button
Upon researching this question further, I find that Guidance Note 3 suggests the 5 x In test is only necessary on RCDs upto 30mA. However I'm struggling to find reference to this in the regulations - I see that 415.1 states that where a 30mA RCD is used for additional protection, it should trip within 40ms at 5 x In - does the fact this isn't stated for other scenarios or other uses of RCDs mean that those other scenarios don't require such testing? (Me being me is likely to test all RCDs as such anyway just for completeness and peace of mind)
Secondly, where in the regulations is it stipulated (or implied or calculated) that the RCD shouldn't trip at 0.5 x In, and that this should be tested?