I know RCDs are covered frequently on this forum, but I've not seen anything else here that describes the type of problem I am having.
In my garage I have a double socket to which a Freezer and Tumble Dryer are plugged in, 2 florescent tubes, and 4 x security lights outside. All of these are connected to the house via a single cable.
The problem we have started to get is that recently when the Tumble Dryer is being used the RCD in the CU trips. I have done a bit of troubleshooting and it appears that the Dryer works fine until the main light in the Garage is switched off (the 2x fluorescents). As long as the lights are kept on it seems to mostly work happily.
However occasionally the RCD trips when the dryer is running and the light isn't switched off, although I suspect it happens when another switch in the house is turned off, or one of the security lights is activated.
I have also noticed that the RCD sometimes trips when the electric fan oven is running (but not the tumble dryer), but that has happened only a handful of times in the last 5 years we have lived in this house and only once since owning the dryer (which is just over a year old).
I noticed the light switch crackled a bit when I switched it so I checked and found that the wires were lose. As I had the switch off anyway I replaced it with a new one.
So then I thought that the dryer might have an earth fault, but if that was the case then why does it mostly work when the garage light is left on?
It's also crossed my mind that the RCD might just be sensitive, but replacements seem hard to come by (or expensive) for my Memera 2000 box. I've seen some used ones on eBay for a few quid but I've no way of knowing if they're any good either, but I might try one anyway.
Anyone have any ideas to what is causing my symptoms? I've included a pic of my CU if that helps at all. If there is any more info you need let me know.
In my garage I have a double socket to which a Freezer and Tumble Dryer are plugged in, 2 florescent tubes, and 4 x security lights outside. All of these are connected to the house via a single cable.
The problem we have started to get is that recently when the Tumble Dryer is being used the RCD in the CU trips. I have done a bit of troubleshooting and it appears that the Dryer works fine until the main light in the Garage is switched off (the 2x fluorescents). As long as the lights are kept on it seems to mostly work happily.
However occasionally the RCD trips when the dryer is running and the light isn't switched off, although I suspect it happens when another switch in the house is turned off, or one of the security lights is activated.
I have also noticed that the RCD sometimes trips when the electric fan oven is running (but not the tumble dryer), but that has happened only a handful of times in the last 5 years we have lived in this house and only once since owning the dryer (which is just over a year old).
I noticed the light switch crackled a bit when I switched it so I checked and found that the wires were lose. As I had the switch off anyway I replaced it with a new one.
So then I thought that the dryer might have an earth fault, but if that was the case then why does it mostly work when the garage light is left on?
It's also crossed my mind that the RCD might just be sensitive, but replacements seem hard to come by (or expensive) for my Memera 2000 box. I've seen some used ones on eBay for a few quid but I've no way of knowing if they're any good either, but I might try one anyway.
Anyone have any ideas to what is causing my symptoms? I've included a pic of my CU if that helps at all. If there is any more info you need let me know.