I have a very recent RCD protected split load consumer unit. The RCD side protects our 3 ring mains only. I live in a rural area with overhead lines and I am on PME.
The problems I am about to describe are all intermittent and we can go several days without problems, then encounter 6 or more occurences in an hour. The RCD never trips without one of the actions below, i.e. we don't wake up in the morning or come home to find it tripped. The weather makes no difference.
* When switching off lights, which are on the unprotected side of the CU the RCD protecting the ring mains will trip. it could be any light but I can almost always make it happen by switching off the pull-cord bathroom light by pulling it down and then 'bouncing' the switch until the RCD goes.
* When using some power tools and my wifes blender the RCD trips. The washing machine/hoover have never caused any probs.
* The garage is on the non-protected side of the CU but with its own separate RCD. When mowing the lawn we come back in to the house to find the other RCD tripped, even though the RCD supplying the mower has not.
With specialist kit I've carried out insulation tests up to 500v, RCD tests and all the obvious connectivity ones. Everything is within spec and as it should be. I have traced all wiring and gone round and made sure all connections are sound and that all metal boxes are properly earthed.
There is reams of stuff on the subject of nuisance RCD tripping but I've not yet seen one that mentions the problems I've been having with the lights.
Has anyone experienced anything like this? Is the bit about bouncing the bathroom light switch significant? I have considered changing over to an earth spike, is this likely to make a difference?
Any comments or help gratefully received!
Thanks
The problems I am about to describe are all intermittent and we can go several days without problems, then encounter 6 or more occurences in an hour. The RCD never trips without one of the actions below, i.e. we don't wake up in the morning or come home to find it tripped. The weather makes no difference.
* When switching off lights, which are on the unprotected side of the CU the RCD protecting the ring mains will trip. it could be any light but I can almost always make it happen by switching off the pull-cord bathroom light by pulling it down and then 'bouncing' the switch until the RCD goes.
* When using some power tools and my wifes blender the RCD trips. The washing machine/hoover have never caused any probs.
* The garage is on the non-protected side of the CU but with its own separate RCD. When mowing the lawn we come back in to the house to find the other RCD tripped, even though the RCD supplying the mower has not.
With specialist kit I've carried out insulation tests up to 500v, RCD tests and all the obvious connectivity ones. Everything is within spec and as it should be. I have traced all wiring and gone round and made sure all connections are sound and that all metal boxes are properly earthed.
There is reams of stuff on the subject of nuisance RCD tripping but I've not yet seen one that mentions the problems I've been having with the lights.
Has anyone experienced anything like this? Is the bit about bouncing the bathroom light switch significant? I have considered changing over to an earth spike, is this likely to make a difference?
Any comments or help gratefully received!
Thanks