Re: Thorn myson apollo CH problem.

Joined
12 Jan 2011
Messages
8
Reaction score
0
Location
Merseyside
Country
United Kingdom
I have been having problems with my ageing apollo 30/50 IT worked fine when set to HW but when set to HW/CH it would cut out aftr 20 minutes and knock the pilot out.Anyhow i replaced the pump last week and it seemed to be ok although I haven`t had it on much due to mild weather. But yesterday I had CH on for a just over two hours when it cut off and is displaying same problem again ok on HW but shuts off on HW/CH. Any ideas or possible solutions please.
 
Sponsored Links
Which heat setting have you set on the boiler?

Tony
 
Sponsored Links
You should measure the flow temperature in each position, probably set for about 82 C and about 68 C.

But the problem is almost certainly with the o/h stat as they tend to ho high resistance. They can be tested by measuring the voltage across them.

However, this is questionable not a job recommended for DIY because it is a safety device controling the combustion of the boiler.

Tony
 