Anybody know where I can find the "reasonable" results for electrical tests

Its a college question

1. The expected test results for a three bedroomed house after complete re-wire (before connection of supply)

Continuity of CPC + main and supplementary bonding
Continuity of Ring Final circuits
Insulation Resistance
Polarity

2. Test results after connection of supply.

PFC
short circuit capacity
Functional testing

EFLI (Live test?)
Ze at origin
Earth electrode resistance

I have not done much testing yet and the OSG give min or max results, so I am unsure of what would be deemed reasonable readings for each of the tests

Cheers
 
Sponsored Links
Look for resistance values of copper (at 20c) and then think about what the lengths of the circuits will be and you should get a reasonable idea. Don't forget the parallel issues with the good old Ring Final.

IR on a brand new installation - think about it................

hope this helps
 
Cheers

OK

Lighting circuit 1.5mm 10 metres


OSG says Resistance/metre or (R1+R2)/metre (mohm/m)

12.10mohms/m

If linked Line and earth at CU does that mean I only measure the one 10m from CU to fitting R1+R2 or do I measure 20m ( line and CPC)

If 10m the reading would be 121 mohms ??
20m 242 mohms ??

IR--- Could damage not be done during installation ?
 
Sponsored Links
Lighting circuit 1.5mm 10 metres


OSG says Resistance/metre or (R1+R2)/metre (mohm/m)

12.10mohms/m

If linked Line and earth at CU does that mean I only measure the one 10m from CU to fitting R1+R2 or do I measure 20m ( line and CPC)

If 10m the reading would be 121 mohms ??
20m 242 mohms ??

1.5mm t&e?
If so, 1.5/1.0 cable has a resistance of 30.20 mohm/m

When measuring R1+R2 you're measuring the resistance of the line and cpc loop so:

(10 x 30.20)/1000 = 0.30ohms
 
Hmmm, maybe crawling around on my stomach under a floor for most of this afternoon reduced my detection of sarcasm :LOL:
 
The suggestion is that there should be maximum IR between conductors.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top