Right, just recently cleared a chimney as flue flow test was failing when Scottish Gas where doing a service on a LFE fire, however everything else was deemed fine. To my knowledge after doing the 2.5 day Scottish Gas induction there is no need for a tightness test when servicing an appliance as LD fluid around the effected connections would suffice.
So, fire re-commisioned now and LD gave slight bubblling at fire connection, which was tightened and now looks fine. But being more cautious, decided to conduct a tightness test and recorded a a 1mb drop over 3 mins.
I know your allowed a 4 mb drop on a u6 over 2 mins, however my question is should I have tightness tested 1st and is the leak size worth worrying about.
Any replys from more experience engineers will be greatly apprectiated, Thanks.