Hello all,
I have a part curiosity question and part second opinion question.
I have a 1950's post war brick house with air cavity.
We are removing the rear wall and installing either 2 Ub's or a single UC section with a plate over. UBs would be be bolted at 600cc through the webs.
The opening created will be fairly large at 5.3m maintaining a 665mm return in compliance with Part A of the BR.
On the rear we will in constructing a single storey extension.
I'm not overly keen on the additional work & cost of installing steel columns which would save us a few hundred mm.
However i did have a think about constructing 440 x 440 solid masonry piers.
As this is less than the 665 return required by the guidance it will need to be justified by calculations.
My question is.... What area of loading should be used when applying the appropriate wind pressures. On the non attached side (semi detached) I don't have any substantial/ continuous internal wall so I assume that the floors provide some diaphragm action taking the load to the central chimney breast.
Therefore if i take the area of half the depth x full height of the house the load and resulting moment on the column will be quite substantial.
The masonry wall at fist floor level will remain so i can consider that looks after itself. Therefore taking half the height of the house x half the depth of the house will result in a much less load and will probably start to make the number work. Does this sound about right? The floor joists and proposed rear roof span parallel to the side wall i'm concerned with so their ability to provide diaphragm action will be limited.
Thoguhts?
Many thanks
I have a part curiosity question and part second opinion question.
I have a 1950's post war brick house with air cavity.
We are removing the rear wall and installing either 2 Ub's or a single UC section with a plate over. UBs would be be bolted at 600cc through the webs.
The opening created will be fairly large at 5.3m maintaining a 665mm return in compliance with Part A of the BR.
On the rear we will in constructing a single storey extension.
I'm not overly keen on the additional work & cost of installing steel columns which would save us a few hundred mm.
However i did have a think about constructing 440 x 440 solid masonry piers.
As this is less than the 665 return required by the guidance it will need to be justified by calculations.
My question is.... What area of loading should be used when applying the appropriate wind pressures. On the non attached side (semi detached) I don't have any substantial/ continuous internal wall so I assume that the floors provide some diaphragm action taking the load to the central chimney breast.
Therefore if i take the area of half the depth x full height of the house the load and resulting moment on the column will be quite substantial.
The masonry wall at fist floor level will remain so i can consider that looks after itself. Therefore taking half the height of the house x half the depth of the house will result in a much less load and will probably start to make the number work. Does this sound about right? The floor joists and proposed rear roof span parallel to the side wall i'm concerned with so their ability to provide diaphragm action will be limited.
Thoguhts?
Many thanks