Symptom:
Boiler fires up for 30 seconds, raises the flow temperature too high and then cuts out. The return pipe eventually gets to just barely warm (after hours of the repeating cycles like that). The first 2 – 3 radiators upstairs heat up ok, with the following 2 – 3 being just barely worm, and with the last 3 being completely cold. The upstairs circuit is separated from the downstairs circuit through a two-port valve.
Theories explored:
1. Radiator Balancing. Not an issue, as the boiler never has a chance even to get to a full power. The flow sensor senses temperature rise too quickly and shuts the boiler down.
2. Pump. Not an issue. There are no problems in the downstairs circuit.
3. Blockage in the pipe work upstairs. Possible, but is it likely? The boiler is a new install (combi for combi swap). The old system worked just fine. The system was power flushed prior to the boiler swap, and it had been clean to begin with anyway. The Magna Clean filter which was installed at the same time was virtually free of anything after 2 weeks running, indicating clean system.
4. Non-return valve installed for the upstairs circuit but not removed prior to closed system upgrade (by prior owners) and the flow/return pipes where mixed up during the boiler swap. This was the best hypothesis, but reversing the pipe connections did not produce any improvements.
The problem appeared after the boiler swap, which was done in the summer months and therefore not properly tested. The original installers refuse to investigate, claiming that they only did the swap and the problem is not boiler, but the central heating system related, which they didn’t touch.
Other heating engineers are puzzled. As described, they have attempted to swap the pipe around hoping to get around a potential non-return valve. It didn’t work, and apart from the lifting carpets and floorboards upstairs, they do not have other suggestions.
Can anyone offer any ideas or tests? What could the boiler swap people do wrong to cause a fault like that?
Boiler fires up for 30 seconds, raises the flow temperature too high and then cuts out. The return pipe eventually gets to just barely warm (after hours of the repeating cycles like that). The first 2 – 3 radiators upstairs heat up ok, with the following 2 – 3 being just barely worm, and with the last 3 being completely cold. The upstairs circuit is separated from the downstairs circuit through a two-port valve.
Theories explored:
1. Radiator Balancing. Not an issue, as the boiler never has a chance even to get to a full power. The flow sensor senses temperature rise too quickly and shuts the boiler down.
2. Pump. Not an issue. There are no problems in the downstairs circuit.
3. Blockage in the pipe work upstairs. Possible, but is it likely? The boiler is a new install (combi for combi swap). The old system worked just fine. The system was power flushed prior to the boiler swap, and it had been clean to begin with anyway. The Magna Clean filter which was installed at the same time was virtually free of anything after 2 weeks running, indicating clean system.
4. Non-return valve installed for the upstairs circuit but not removed prior to closed system upgrade (by prior owners) and the flow/return pipes where mixed up during the boiler swap. This was the best hypothesis, but reversing the pipe connections did not produce any improvements.
The problem appeared after the boiler swap, which was done in the summer months and therefore not properly tested. The original installers refuse to investigate, claiming that they only did the swap and the problem is not boiler, but the central heating system related, which they didn’t touch.
Other heating engineers are puzzled. As described, they have attempted to swap the pipe around hoping to get around a potential non-return valve. It didn’t work, and apart from the lifting carpets and floorboards upstairs, they do not have other suggestions.
Can anyone offer any ideas or tests? What could the boiler swap people do wrong to cause a fault like that?