Lectrician said:A DOL starter with a reverse function.
It has two 3 pole contactors, the outputs of which are commoned up, before they hit the overload. The supply to both contactors is also commoned up, except on one contactor the L1 and L2 are reversed. Two green start buttons, one forward, one reverse.
There is also a 'fourth auxiliary' pole which opens when the contactor energises. This is in series with the start button of the opposite contactor. This prevents the second contactor from energising.
Swapping ANY two phases of a 3 phase motor will reverse the direction.
Lectrician said:A Motor should generally be protected by a DOL starter.
Lectrician said:A DOL starter (dirct on line) is basically a contactor with an overload incorporated. The overload is selected depending on the FLC of the motor (full load current). The overload is adjustable to half an amp usually.
If the motor is mechanically overloaded, the current rises, and the overload will 'trip' the contactor and turn the supply off.
Some motors also have thermistors burried in the windings, and these can be incorporated into the control circuit to trip the contactor if the windings overheat.
A DOL starter has a green and red button on the front of the enclosure, and the contactor and overload inside.
An MCB will offer little protection against mechanical overload of a motor.