Whilst I'm no champion of ring circuits, it obviously remains the case that smaller cable (2.5mm²) can usually be used for a ring final protected by a 32A MCB than would be required for a radial circuit protected by a 32A MCB. Whether that is sufficient reason for using a ring is a different question!They were introduced to allow smaller cable to be used with 30A rewireable fuses - (metric equivalent 2.5mm² instead of 6mm²). With MCBs this does not apply.
I never quite see the validity of that argument when it applies to no other circuit.Ring finals also offer the advantage of CPC redundancy,
You mean just "radial" ?The radial ring (2.5mm² with 20A fuse) downstairs
I don't quite understand your point. Ring finals and (some) circuits with explicit 'high integrity earthing' are the only ones which have this feature - which, in itself, enhances safety. So, yes, that 'safety feature' does not exist in relation to any other types of circuit - but that doesn't alter the fact that, in those two situations, it does (in that one respect) enhance safety.I never quite see the validity of that argument when it applies to no other circuit.Ring finals also offer the advantage of CPC redundancy,
I do not know if it is true, but stillp is always telling us that it was a significant consideration in relation to the introduction of ring finals.My point is that CPC redundancy is not a consideration when installing circuits.
Neither do I. It doesn't really make sense.\I do not know if it is true, but stillp is always telling us that it was a significant consideration in relation to the introduction of ring finals.
In the absence of downsides, CPC redundancy obviously makes sense (just as does the {I presume} dual braking system you have in your car). As for the downsides, given the 'margins' we often discuss, and given how unlikely it is that both L and N rings would be broken simultaneously (unless by human act!), I don't think there is really an appreciable risk of 20A CCC cable being 'seriously overloaded'. Of course, if (as commonly) the CCC is 27A, I would say that the chances of a 'serious overload' are then virtually non-existent.Neither do I. It doesn't really make sense.\I do not know if it is true, but stillp is always telling us that it was a significant consideration in relation to the introduction of ring finals.
Well, I have retired but -Do I take it that, unless explicitly asked to by a customer, you would not install a ring final new circuit?
Fair enough.Well, I have retired but - I would not - unless the route was very favourable - as above.Do I take it that, unless explicitly asked to by a customer, you would not install a ring final new circuit?
As I said, I'm no champion of ring finals - so, no, I would not argue that. However, what I would argue is that IF one would feel more comfortable with CPC redundancy, then one should implement it, one way or another (but should also take into consideration any downsides of the method of implementation one chooses).If you are now going to argue for ring finals wherever possible, for that reason, then perhaps we could have T&T (Twin & Two earth, instead of T&E) for radial circuits.