Evening folks.would 600mm centres be ok for a garage roof,4m span with 8x2 rafters.
No. I think you are just under (C24) at that span. At 450mm c/c (C24) you may just nick it.Evening folks.would 600mm centres be ok for a garage roof,4m span with 8x2 rafters.
Neither of the tables you linked to permit 4m with 8x2 C16 and 0.75/0.75 loadings?Not sure if you are flat or sloping roof but these tables will help
Depends on the loadings, lighter weight constructions of not-regularly-walked-on will be acceptableNo. I think you are just under (C24) at that span. At 450mm c/c (C24) you may just nick it.
So two overweight blokes, a few rolls of felt and a full bottle of gas, is a no-no.Depends on the loadings, lighter weight constructions of not-regularly-walked-on will be acceptable
Never said they did, just some reference tables that don't flag up 200 x 50 joists either just to give him a feel for things but thanks for the heads upNeither of the tables you linked to permit 4m with 8x2 C16 and 0.75/0.75 loadings?
Plastic roof with no footpaths then?Depends on the loadings, lighter weight constructions of not-regularly-walked-on will be acceptable
In that case have as many footpaths as you wantThanks peeps for your input.just gonna go 400mm spacing I think with 18mm osb.only a garage at the end of the day
Ah, I thought your first paragraph was giving the deflection etc you'd calculated from the OP's spec, plus some assumptions, and declaring the proposed joists to be just on the right side of acceptable..Never said they did, just some reference tables that don't flag up 200 x 50 joists either just to give him a feel for things but thanks for the heads up
I was but not from the OP spec as he only gave a joist size, but from my loading assumptions which showed with the loadings assumed the joist size to comply with acceptable parametersAh, I thought your first paragraph was giving the deflection etc you'd calculated from the OP's spec, plus some assumptions, and declaring the proposed joists to be just on the right side of acceptable..
Are you running your calcs on a 200x50 size?I was but not from the OP spec as he only gave a joist size, but from my loading assumptions which showed with the loadings assumed the joist size to comply with acceptable parameters