Hello, my architect has designed the following extension for me. They have specified a cold pitched roof (with insulation between and below rafters). They have also specified a breathable sarking felt (my architect has said Nilvent is good to use). The architect has also specified that sufficient ventilation should be provided at the ridge. (monopitch roof flashing vent or high level vent tile) and sufficient ventilation at the eaves (25mm continuous ventilation over at eaves) .
My builder is saying that because I am using a breathable membrane, which lets air in anyway, there is no need for ventilation gaps at the eaves or ridge. My architect disagrees with him. (one thing my architect said is that you need both, but the ventilation gap over insulation does not have to be as big with a breathable membrane. Also said that in cold, water in breathable membrane could freeze, so no longer breathable at times, hence need for ventilation.
who is correct?
My builder is saying that because I am using a breathable membrane, which lets air in anyway, there is no need for ventilation gaps at the eaves or ridge. My architect disagrees with him. (one thing my architect said is that you need both, but the ventilation gap over insulation does not have to be as big with a breathable membrane. Also said that in cold, water in breathable membrane could freeze, so no longer breathable at times, hence need for ventilation.
who is correct?