hi can anyone help please i have a fer falcon combi boiler with no stat fitted by last owners i brought danfoss rmt 24 volt do i fit two wire from stat to boiler and remove link :confused:
 
Sponsored Links
I have a fer falcon combi boiler with no stat fitted ... I bought danfoss rmt 24 volt. Do I fit two wire from stat to boiler and remove link :confused:
The Falcon requires a thermostat with volt-free contracts. The RMT24 is not suitable as it needs 24V and a neutral connection.

You need the Danfoss RET B.

Remove the link at the boiler and connect terminals 2 and 3 of the thermostat to the same terminals. It does not matter which way round the wires go.
 