Hi
We are removing a load bearing wall (supports first floor joists only) and have had a SE come in a do the calc. There is a door in the supporting wall and when we removed the load bearing wall we found a lintel across the door way exactly where the padstone would sit, thankfully it meets the specs of the SE calc. The only issue is as this was alreay in place it is about 6-8mm too low so is it ok to pack the gap with a strong mortar mix or should some form of shims be used. The beam is currently acro propped in place. My concern about shims it evenly distributing the load to the padstone and I also have no idea where to get shims.
If I do use mortar what mix should I use
Thanks in advance
sully
We are removing a load bearing wall (supports first floor joists only) and have had a SE come in a do the calc. There is a door in the supporting wall and when we removed the load bearing wall we found a lintel across the door way exactly where the padstone would sit, thankfully it meets the specs of the SE calc. The only issue is as this was alreay in place it is about 6-8mm too low so is it ok to pack the gap with a strong mortar mix or should some form of shims be used. The beam is currently acro propped in place. My concern about shims it evenly distributing the load to the padstone and I also have no idea where to get shims.