I posted that because I wanted anyone who came here looking up "safe zones" to get the right information. EG, someone may end up here wondering if the work done in their kitchen was to regulation. Yes, 523-20(d) does talk about protecting cables outside of the safe zones. .... But that goes hand in hand with cables inside safe zones.
And I wanted to be certain that anybody reading this was not confused by: .... I know you meant something like "... and didn't allow 'diagonal' routes between two visible accessories to be included in the safe zones" .... Just a bit of clarification, that's all!
Fair enough. As the person who's questions really started this, I feel inclined to try to 'clarify the clarification', since I think there may still be some scope for some people to get confused.
As far as I can make out (and please correct me if you think I'm wrong), I think the situation is quite simple, and that nothing has really changed since the aspects of the regs we are discussing first appeared some 35 years, namely ...
1... Prior to implementation of 15th edition (1981-85), there were no explicit 'rules' about buried cables, the closest being the vague requirement that cables should be adequately protected against mechanical damage "in normal service" - and it's not clear (at least, not to me) as to whether 'normal service' was intended include attacks with drills, screws, nails etc.
2...Ever since then (hence throughout 15th, 16th, 17th & 18th eds.) there has been an essentially unchanged/unchanging provision for cables to be buried without mechanical protection (e.g. steel conduit) or an earthed covering in the specified 'zones'. Although we speak of them as 'Safe Zones' (which I personally regard as a misnomer - certainly for anyone with a drill, nail or screw in their hand!), I don't think that any edition of the regs has ever used or mentioned that term (merely 'zones').
3...Those zones consist of, and always have consisted of, the top 150mm of walls and the 150mm within the angle formed by two adjacent walls , and straight cable runs which are aligned horizontally or vertically with visible accessories. These zones have never included diagonal routes between accessories.
Do you agree with all that?
One point perhaps worthy of comment/question is that most people seem to regard the 150mm zone created by the angle between two adjoining walls as applying only to 'internal corners', whereas it would seem that the wording of the regulations, from 15th through to 18th eds., could probably be interpreted as also applying to 'external corners'. What do people think about that?
Kind Regards, John