hey i wonder if anyone can help me out with a few regs. i need to supply power for 8 treadmills in a gym. they are situated in the middle of the room with a pillar at either end of the 8 and there is a suspended ceiling above and a solid concrete floor below. i want to run my cables on a tray above the ceiling, down the pillars in some sort of trunking and i was wondering if there is any type of surface trunking i can use along the floor in front of the machines or whether the floor needs to be chased and cables buried because of a tripping hazard from trunking. many thanks
 
Sponsored Links
I think you already know the answer - burying the cables is by far the best solution. Obviously you could use rubber cable protectors/ramps/profile or whatever you prefer to call it, but this isn't really what I'd consider a permanent solution.

If you really can't bring yourself to chase the floor then it would probably be better to drop down from the ceiling above the treadmills, although I imagine it would look rather gash.
 
Not sure how much electricity a treadmill requires, but if they are low consumption (<500w), run a couple of 4-way leads down from the ceiling next to them.
 
I never did see a gym with cables coming down from the ceiling.

Looks OK in a machine shop but I'd like an uninterrupted view of the TV when I'm at the spinning class.
 
Sponsored Links
I meant drop it down the side of the machine, perhaps zipped to the frame of the treadmill, hence not interrupting the TV view. ;)
 
Do you know what the protective conductor current of the treadmills is? They might need high integrity earthing, in which case a 13A socket is not much use.
 
Do you know what the protective conductor current of the treadmills is? They might need high integrity earthing, in which case a 13A socket is not much use.

If they're supplied with a 13A plug fitted then there's no problem feeding them from a 13A socket. I very much doubt the CPC current in a single treadmill is going to be any cause for concern, and that's assuming they aren't double insulated. If it's a worry when the protective conductor currents of the multiple loads are combined, a high integrity ring final or radial can be used to feed the outlets.
 
I came across some last year that had protective conductor currents >10mA in spite of being supplied with a fitted 13A plug.
They contained variable frequency inverters with EMC filters.
 
Do you know what the protective conductor current of the treadmills is? They might need high integrity earthing, in which case a 13A socket is not much use.

As a new member to the forum there is a rule that if you mention HIE you have to be able to tell us how to install it :evil:
 