AFAIAA, although it's perhaps a little surprising, you are right in saying that there is no equivalent of 522.6.202 - 522.6.204 (cables buried in walls) for cables buried in floors. However, in a more general sense, 522.6.1 requires measures to minimise risks due to mechanical damage, including penetration - and I personally would not think that would be satisfied by, say, T+E buried without adequate mechanical protection within, say, 50mm of the surface of a concrete floor, would you?Why earthed metal covering? As far as I am concerned this is not required, and the cable could go straight in the floor ...
Indeed - in fact, as far as electrical considerations (rather than re-wiring) are concerned, directly buried in the concrete without any conduit would presumably be OK - i.e. directly analogous to the requirement for cables buried in walls.I would like to see the cables at least 50 mm from the surface of the concrete. ... If that depth or greater, I would be happy for the cables to be in PVC conduit ...
Sure, my instinct says the same.I guess some discretion can be used about the depth of the cable, and likelihood of it getting penetrated, as it's not a wall, but instinct tells me 50 mm deep is LESS likely to get drilled.
Yes, I understand that - and if it were possible to bury unprotected T+E >50mm deep without compromising the floor in any way, then that is probably the simplest approach.Ultimately I would like to save the op the trouble of using earthed metal conduit or similar - if one is inexperienced in this a right mess could be created. SWA could be used, but again could be done extremely wrong by the inexperienced.
If the cable is buried at a depth of less than 50mm then it must be in an earthed metallic protection.
Why are you going over this ground which has already been discussed in this thread? Even though what you say is sensible/reasonable, in contrast with the situation with walls, AFAIAA there is no regulation which imposes any explicit requirements in relation to cables buried in floors.If the cable is buried at a depth of less than 50mm then it must be in an earthed metallic protection.
Ironically, if the cable passes through a joist or batten <50mm from the top (which might well violate other Building Regs), there is such a requirement (or alternative), since 522.6.201(ii) invokes 522.6.204 (the same reg we are very familiar with in relation to walls)!We all have cable buried under our floorboards and there is no requirement for "earthed metallic protection".
If the cable is buried at a depth of less than 50mm then it must be in an earthed metallic protection.
Says who, and under what circumstances?
We all have cable buried under our floorboards and there is no requirement for "earthed metallic protection". What scenarios / regulations are you quoting?
Why are you going over this ground which has already been discussed in this thread? Even though what you say is sensible/reasonable, in contrast with the situation with walls, AFAIAA there is no regulation which imposes any explicit requirements in relation to cables buried in floors.If the cable is buried at a depth of less than 50mm then it must be in an earthed metallic protection.
Kind Regards, John