PROBLEM.
That could be what the end result "looks like".
However there are *MANY* critical technical details affecting the design.
These are related to compliance with BS7671 AND to safety.
There are no DIY kits due to those critical technical details.
SOLUTION.
1. Introduction.
Read the IET doc, join the following text & paste into webbrowser.
http://www2.theiet.org/Publish/WireRegs
/WiringMatters/Documents/Issue16/2005_16
_autumn_wiring_matters_electrical_installations_outdoors.pdf
2. Decide who does what.
From your posting I suggest you use option b).
a) you Design, Install, notify labc for I&T (inspect&test)
b) spark Designs, you Install, spark connects, I&T
The reason is you do not know what you do not know yet must know.
Not an insult, running an outside cable has many technical considerations.
I do not think your spur off (probably) a ring for a welder is sound.
You will probably need a dedicated feed from an RCBO in your CCU.
EXAMPLE - Technical Details.
1. Identify shed environment re earthing & house earthing type.
a) If the house is TT, you make the shed TT with its own local earth rod.
b) If the house is PME, you make the shed TT with its own local earth rod if any of i) concrete floor ii) class-1 tools iii) incoming metal service pipe.
c) If the house is PME, you export the earth to the shed if the floor is wood, no metal structure in contact with the soil, only class-2 tools, no incoming metal service pipes.
Technical details are critical.
Why?
Suppose you export your house PME earth to a shed and use a Class-1 earthed metal cased tool outside, eg, WELDER.
- WELDER metal casing is now at house PME earth potential.
- Soil at the shed may be at a different potential.
- Potential difference between tool & soil, hands & feet.
If the potential is sufficiently high 30ma could flow.
- Now that might trip your 30ma RCD, but if faulty you could die (30ma right on edge of ventricular fibrilation).
- Yes the test button may work, but that does NOT mean it is in spec re 0.5/1/5x at 0-180-degree phase tests etc.
2. Identify if MEB is missing or needs upgrading.
MEB is Main Equipotential Bonding
- MEB Must be present & sized correctly for your supply type
- MEB is a Gr/Ye earth wire linking MET (Main Earthing Terminal) to Gas & Water Pipes
If MEB were missing.
Street digger damages supply Neutral, fails months later.
- Earthed appliances in the house are now at Uo supply potential (230V)
- Water tap & Gas pipe fed by metal piping are at ground potential (0V)
- Hand on metal tap (Uo), hand on tap to lead water main (0V) = dead.
- Hand on metal WELDER at shed (Uo), feet on soil (0V) = dead.
That is why DNO have a fit if they see no MEB.
Even if the MEB is too small, it could be a problem (the copper could melt before the PME main fuse blows).
3. Voltage Drop, EFLI, Cable Sizing, Cable Factors for routing inside.
There are no DIY kits because of the *install specific details*.
These details are not "idealistic", but critical re safety.
Impossible to remote design without seeing an installation, so much information is needed.
- House supply type
- CCU type re age/rcd present/spare ways
- cable routing options
- shed load
- cable sizing after applying Ca Ci Cf Cg grouping factors within house for route
- Vdrop calculations
- EFLI calculations & verification at i&t re r1+r2, zs etc
- Earthing method re remote TT or export-PME
- Isolation
- CPD selection since it is a WELDER
Current welder (or future) may impose a load which may preclude use of Type-B trip characteristics.
That may necessitate other trip characteristics, with resulting cable re-sizing for Vdrop & EFLI to ensure the CPD trips. Fit a Type-C breaker in place of Type-B and if EFLI is not low enough your cable becomes the fuse protecting the CPD!
It really is not a trivial task, involving complex designwork particularly since a Welder is involved.
Hence easy answers or DIY kit are not quick to appear.
Go read the IET PDF document.
Then pick up an electricians guide.
Then speak to a spark, you will at least understand them better and WHY certain things are needed.