college lecturers no nothin... again.
basically, i say:
test circuit is live
switch off
check dead
test tester on known supply/proving unit
lock supply off/keep key
they say this is wrong and it must be:
switch off
test tester on known supply
check circuit is dead
test tester on known supply
lock off
for some reason, they think its wrong to test the circuit to be isolated before starting saying you must not. now, what happens if its fed from DB 1 and has tripped. you 'think' its fed form DB 2 and switch something at the other side of building off and lock off. someone notices something off and investigates. they go to DB1 and notice something off, so switch on. you then get a shock, since you locked off DB 2. apparantly, this will never happen.
so, which, if any, would you say is right?
basically, i say:
test circuit is live
switch off
check dead
test tester on known supply/proving unit
lock supply off/keep key
they say this is wrong and it must be:
switch off
test tester on known supply
check circuit is dead
test tester on known supply
lock off
for some reason, they think its wrong to test the circuit to be isolated before starting saying you must not. now, what happens if its fed from DB 1 and has tripped. you 'think' its fed form DB 2 and switch something at the other side of building off and lock off. someone notices something off and investigates. they go to DB1 and notice something off, so switch on. you then get a shock, since you locked off DB 2. apparantly, this will never happen.