salus wireless thermostat

Joined
2 Nov 2014
Messages
3
Reaction score
0
Location
Sussex
Country
United Kingdom
Welcome all. I'm hoping someone can help me out with connecting new wireless stat with connection: L,N, COM, NO in place of the existing old honeywell stat that has only two wires: perm live and SL. Also there is honeywell programmer, seperate for HW and HTG, that has 8 connectors L,N, NO, NC(not connected), COM, last 3 are double for HW/HTG. Whole system is sundial S with 2 valves. I was thinking to leave programmer in place to control HW and set HTG on constant then use wireless to program/temp. Obviously I know where to get L/N. It would be great if someone could point me in the right direction.
regards
 
Sponsored Links
Make sure the Live and Neutral to the new stat receiver are taken from the wiring centre.
If you can identify the Switched Live connection in the wiring centre (SL that went to the old room stat) it should be connected to NO in the new one plus a short link will be required to extend the live across to the COM terminal.

With the above arrangement the old programmer should have no effect on the central heating.
 
Any particular reason you're replacing the Honeywell with a Salus? Seems a bit of a downgrade to me!
 
thanks for replies so far. well current stat is propably 30 years old and is in the hall and is very difficult to control temperature in living room/bedrooms as hall gets colder. so I'm looking to control the temp by wireless stat where req. By wiring centre do you mean box in bedroom near valves and pump?
regards
 
Sponsored Links
If that's where all the boiler pump and programmer etc wiring is brought together it will be the best place for the new receiver.
 
Hello!! Thanks jackthom. I've done the job as per your advice, works as intended. But I have a concern about the fuse/spur that isolate heating as is 3amp as required for honeywell programmer but now I have salus wireless programer connected to that circuit and that requires 5amps. would you recommend changing the fuse?
regards
 
The Salus unit won't require anything near 5 amps to run and will be perfectly OK sharing power from the existing 3A fused supply in the wiring centre.
 