Servicing your alarm system, the basics .......

Joined
20 Nov 2007
Messages
2,954
Reaction score
268
Country
United Kingdom
Servicing your alarm system, the basics .......

1: MAINS PHASE NEUTRAL TEST. AC voltage between Live
and Neutral.
This should measure between 220 - 250VAC.
MAINS PHASE EARTH TEST: AC voltage between Live and
Earth.
This should be the same as the previous reading.
MAINS NEUTRAL EARTH TEST: AC voltage between
Neutral and Earth.
This reading should not exceed 1.2VAC.

2: POWER SUPPLY TEST: Transformer AC voltage output.
This should measure between 14 - 21VAC.

3: POWER SUPPLY CURRENT NORMAL TEST: AC current used
by system when unset.
Measure with meter in series with the transformer
output.

4: POWER SUPPLY CURRENT IN ALARM TEST: AC current used
by system when in alarm. As step 3.

5: INDUCED AC TEST: AC voltage between DC+ and earth.
AC noise should not exceed 1.2 volts max.

6: BATTERY CHARGING VOLTAGE TEST: DC voltage at
battery terminals.
Measure with charge leads connected to the battery.

7: PANEL AUXILIARY DC VOLTAGE TEST: DC voltage supply
to detectors.
Should be within ±1volt of the battery charging
voltage.

8: BATTERY FLOAT CHARGE TEST: DC mA current flowing
through battery.
Should fall from a double mA figure to a single mA
figure within 30 seconds.

9: BATTERY SYSTEM CURRENT NORMAL TEST: DC current used
by system when unset.
Ideally, not more than 5% of the batteries Ah
capacity.

10: BATTERY SYSTEM CURRENT IN ALARM TEST: DC current
used by system when in alarm. Ideally, not more
than 10% of the batteries Ah capacity.

11: BATTERY TEST: Record Temperature, Voltage °C DCV Ah
and Capacity available. Replace battery when
reading falls below 65% of Ah capacity.

12: CIRCUIT RESISTANCE TESTS: Record all circuit
resistances. Circuits must be removed from control
panel before testing.

13: CIRCUIT EARTH LEAKAGE TEST: Check for resistance
between zone, tamper and earth. Test with meter on
highest Meg Ohm range.

14: BELL TAMPER RETURN TEST: Record resistance between
0Volt and removed tamper return. Check for stable
resistance. Ring bell to induce vibration.

15: PANEL ZONE WALK TEST: Walk test all detection zones
to confirm operation.
Check each circuit operates normally, especially
after lightning.

16: SELF-ACTIVATING BELL TEST: Remove hold-off voltage
to confirm operation. Replace if defective.

17: BELL & STROBE TEST: Activate bell and strobe to
confirm operation. Replace if defective.

18: WIRING AND CONNECTIONS: Check panel for incorrect
or loose wiring connections. Check all cables are
marked and connected correctly.

19: DETECTOR VOLTAGE TEST: Check voltage at furthest
detector is above 13VDC.
Low or unstable DC voltage at the detector is a
main cause of false alarms.
 
Sponsored Links
The answer to your question is the first line of my post.
 
Sponsored Links
That's not the 'original' I copied from, but it is from the same company.

This is supposed to be a DiY Forum, the 'basics' was/is for the DiYers, not for any Pro, they should know all this any way.
 
That's not the 'original' I copied from, but it is from the same company.

This is supposed to be a DiY Forum, the 'basics' was/is for the DiYers, not for any Pro, they should know all this any way.

I'm only trying to find out what should happen when my alarm system is serviced. Its better to be in the know imo.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top