I started with the title which seems to make the distinction of multicores, or, circuits of singles. Deliberately turned round for emphasis. .... Then the heading makes more sense.
[ it's slightly different in the current version of the regs, since the mention of "singles" has disappeared from both Table title and column headings ]
Anyway, you seem to be saying exactly the same as I did. You took a title which, as written, is difficult to make sense of (and/or is ambiguous) and modified it into something which "made more sense". However, that was just a decision on your part, which may or may not correspond with the intent of the regs. As I illustrated, you could have modified it in a different way, again resulting in something which made much more sense, but with a very different meaning. How can we tell which is correct?
If the consensus is to ignore the table, where do we stop ignoring the regs?
I'll talk a bit about the general situation below but, in the specific current context, as the disagreement between EFLI and yourself illustrated, one cannot even know whether or not one
IS "ignoring the reg" (actually "ignoring guidance in a non-Normative Appendix of the regs"? We can presumably agree that, in the case of, say, a ring final, one can have "
two multicore cables" which relate to "
one circuit" - so, if it is just those two cables that are concerned, which column of 4C1 do we look at - the one headed "Number of circuits or multicore cables = 1"
OR the one headed "Number of circuits or multicore cables = 2" ??
Also, as I asked, how can we work out if/when any of the grouping factors in the table are "applicable" (and hence whether one is "ignoring the guidance"), given ..
NOTE 1: These factors are applicable to uniform groups of cables, equally loaded.
??
So, it's not really a question of whether or not one "ignores" the guidance but, rather a problem in working out what the guidance is trying to say! In such an (unsatisfactory) situation, the best one can do is to try to make a judgment as to what the guidance is trying to say - and, as EFLI and yourself have illustrated, different people may come to different conclusions.
If the consensus is to ignore the table, where do we stop ignoring the regs? Why not save money and use 4mm² (and a 40A OCPD) as that is rated at 40A (ref1) for the 42A (potential) load? In fact why not abandon the regs altogether, use 2.5mm² and not bother with those expensive things in the box that cause so many questions on this forum? After all it is a resistive load that's impossible to draw over current and the DNO does provide a fuse.
In many senses, this is an inappropriate discussion to be having in this forum, since the 'official line' has to be that one should follow the regs (and maybe even accompanying 'Informative guidance') to the letter, and a good few electricians are also constrained (by conditions of employment and/or scheme membership) to do just that.
For a start, to be able to do that requires that the regs should be clear, unambiguous and comprehensive and, above all, that they should correspond with 'electrical common sense' - which, unfortunately, is sometimes very far from the case.
Has it ever occurred to you that the reasons for the Appendices of BS7671 are only "Informative Guidance" (rather than "Normative") might be to allow 'flexibility' (individual judgement) on the basis of 'electrical common sense'?
For example, in context, do you really think that it would be reasonable/necessary (or consistent with 'electrical common sense') to, say, substantially de-rate the CCC of a 30 metre length of cable because a couple of inches of it were 'grouped' with some other cables, particularly if the cable was never going to be carrying any current for more than a few minutes?
Kind Regards, John
-