ajl said:the guide suggests cable size for various lenghts of cable run. it does not refer,or i cant see it, to the size of the shower ie 7.5 8.5 9.5 10.5 kw. is this therefore not an issue?
The "How To" guide assumes they are all 7.2kW...andrew2022 said:you select the cable taking total power, cable length, installation mehtod (thru insulation, clipped direct etc etc) into consideration. the size of the shower is the most important factor here.
//www.diynot.com/pages/el/el053.phpmapj1 said:whos how to? If its this site should Email admin and say...
Not really - if the shower is rated at 8.5kW at 230V, then it will be just slightly over the 36A rating. Not good to run MCBs flat out - go for a 40 or 50A one.ajl said:will a 36a trip be sufficient,
Sounds like an RCD. 32mA? or 30mA? Whatever - I have no idea if French regs require one, but even if not they are a Jolly Good Idea. But get him to fit a 50A one as insurance against the day you decide to fit a more powerful shower....and the french guy here want to fit a 40a 32ma differencial????? what ever that does???
Might that be because of the electricity charging structure? Paying for a supply capacity of 50A when you only need that much for 30 minutes a day?ajl said:by the way i have not yet seen electric showers for sale here.???