Hi Guys...
My mate wants to install an En - suite shower and also to utilise his loft space for use as a study / bedroom (1 x Ring Main + Lighting)....the work has been notified to the LBA and work has commenced on the Central Heating for the study / bedroom....
He has asked me to have a look and advise as to the shower size....however...on inspection, I have noted...
Mains - 100A Split Load 9 way Consumer Unit fed via 25mm Tails from 100a Fuse on suppply...
Non RCD side - feeds the cooker (32A MCB) + Immersion (16A MCB) + 2 x 6A MCBs for lighting...+ 1 x spare way....
RCD Side - 63A 30mA - feeds 2 x downstairs ring mains (Kitchen / front room) via 32A MCBs + 2 x Spare ways
I obviously need to check and confirm that designated circuits are what they say they are !!....and potentially change if reqd...(Immersion etc)
Regarding the Shower unit and ring main and lights....specifically noting the 63A limitation on the RCD - and looking to keep any shower feed to 10mm - what do you advise re the circuits in the CU ....would 63A RCD be sufficient to allow for another ring main (study) + Shower ? if so, would it also need be limited to less than 10kW ? (10mm)
Advice appreciated...TA very much...[/b]
My mate wants to install an En - suite shower and also to utilise his loft space for use as a study / bedroom (1 x Ring Main + Lighting)....the work has been notified to the LBA and work has commenced on the Central Heating for the study / bedroom....
He has asked me to have a look and advise as to the shower size....however...on inspection, I have noted...
Mains - 100A Split Load 9 way Consumer Unit fed via 25mm Tails from 100a Fuse on suppply...
Non RCD side - feeds the cooker (32A MCB) + Immersion (16A MCB) + 2 x 6A MCBs for lighting...+ 1 x spare way....
RCD Side - 63A 30mA - feeds 2 x downstairs ring mains (Kitchen / front room) via 32A MCBs + 2 x Spare ways
I obviously need to check and confirm that designated circuits are what they say they are !!....and potentially change if reqd...(Immersion etc)
Regarding the Shower unit and ring main and lights....specifically noting the 63A limitation on the RCD - and looking to keep any shower feed to 10mm - what do you advise re the circuits in the CU ....would 63A RCD be sufficient to allow for another ring main (study) + Shower ? if so, would it also need be limited to less than 10kW ? (10mm)
Advice appreciated...TA very much...[/b]