Hi
My shower keeps tripping off at the Consumer box. It does not do it straight away only when the shower has been on for a while (Approx 10mins) but it is random so its sometimes longer. Happens quicker the hotter I have the water. I dont remember it happening when the shower first went in. Seems to be happening more and more frequently.
I had a 8.5kw shower, which I replaced with a Triton Bezique 9.5kw. I believe the cable is a 6mm (how can i double check this?)
Cable lenght is approx 38ft long, Fuse box to shower.
I have a switch along this cable between the consumer box and shower.
On the consumer box (See photo) there is a fuse which the shower is wired into. On the side it reads " 240v - CaL Temp 20degrees - Type B - 5A M1 - 15A-45A M2" On the red button that pops out when shower has tripped it says "30a"
I have not changed anything but the shower, just took the old one off and put the new one on. I thought it would be fine as I read on the net that a 9.5kw shower is ok on 6mm cable. Is there a chance the fuse is faultly? My electric cupboard is very old but never had any problems with the old shower. Although sometimes if the kettle, washing machine and tv are all on at the same time the plugs trip off in the consumer box. Must be overloading which could be happenening to the shower?!
Thanks!
My shower keeps tripping off at the Consumer box. It does not do it straight away only when the shower has been on for a while (Approx 10mins) but it is random so its sometimes longer. Happens quicker the hotter I have the water. I dont remember it happening when the shower first went in. Seems to be happening more and more frequently.
I had a 8.5kw shower, which I replaced with a Triton Bezique 9.5kw. I believe the cable is a 6mm (how can i double check this?)
Cable lenght is approx 38ft long, Fuse box to shower.
I have a switch along this cable between the consumer box and shower.
On the consumer box (See photo) there is a fuse which the shower is wired into. On the side it reads " 240v - CaL Temp 20degrees - Type B - 5A M1 - 15A-45A M2" On the red button that pops out when shower has tripped it says "30a"
I have not changed anything but the shower, just took the old one off and put the new one on. I thought it would be fine as I read on the net that a 9.5kw shower is ok on 6mm cable. Is there a chance the fuse is faultly? My electric cupboard is very old but never had any problems with the old shower. Although sometimes if the kettle, washing machine and tv are all on at the same time the plugs trip off in the consumer box. Must be overloading which could be happenening to the shower?!
Thanks!