Information required please,
I have a 9.5 KW shower which is powered from the consumer unit with a Wylex 63amp load /30ma trip RCD through a 40amp MCB then on to 50amp MK pull switch then to the shower all run in 10mm cable. Distance from consumer unit to shower approx. 15 meters with wiring run through cavity wall then through loft.
My question is following a problem with burnt neutral wires in the consumer unit which my electrician said was almost certainly caused by a loose connection as he found others loose I have noticed that when having a shower the neutral wire is getting warmer than the live wire.
Using a non contact thermometer at the consumer unit connections the live wire is approx. 25degrees whilst the neutral is around 46degrees also if you touch the RCD casing the neutral side is warmer.
All shower terminals have been checked and tightened and the shower has been in use for approx. 8years,
Is this normal and I am being paranoid or do you think I have a problem somewhere and if so any suggestions before I call the electrician back.
AS far as I know it could have been like this for years and never noticed.
Sorry to drag on but tried to give as much info as poss to start off with.
Thanks Dunc.
I have a 9.5 KW shower which is powered from the consumer unit with a Wylex 63amp load /30ma trip RCD through a 40amp MCB then on to 50amp MK pull switch then to the shower all run in 10mm cable. Distance from consumer unit to shower approx. 15 meters with wiring run through cavity wall then through loft.
My question is following a problem with burnt neutral wires in the consumer unit which my electrician said was almost certainly caused by a loose connection as he found others loose I have noticed that when having a shower the neutral wire is getting warmer than the live wire.
Using a non contact thermometer at the consumer unit connections the live wire is approx. 25degrees whilst the neutral is around 46degrees also if you touch the RCD casing the neutral side is warmer.
All shower terminals have been checked and tightened and the shower has been in use for approx. 8years,
Is this normal and I am being paranoid or do you think I have a problem somewhere and if so any suggestions before I call the electrician back.
AS far as I know it could have been like this for years and never noticed.
Sorry to drag on but tried to give as much info as poss to start off with.
Thanks Dunc.