Coming to the problem fresh, I imagined that there will be a 'sweet spot' for insulation sizing for each size of pipe and for each ΔT that reflects the law of diminishing returns.
Has anyone already done calculations on heat losses that can validate or refute my approach to this?
Using the formula: Q = 2*(pi)*k*L(T1-T2/[ln(r2/r1)]
Where Q = heatloss, k is thermal conductivity of insulator, L is pipe length, T1 & T2 are ext and internal temps, ln is natural log, and r2 & r1 are outer & inner radii of the insulation. Using 0.038 as k (for Armaflex at 40degC) & for 22mm copper with ΔT70 I get 36W loss per metre with 13mm Armaflex and still 22W with 25mm Armaflex.
This is rather higher than I imagined I would find, even using the best and most expensive pipe insulation available for domestic settings. What do others think? Have I made a methodological or calculation error?
Has anyone already done calculations on heat losses that can validate or refute my approach to this?
Using the formula: Q = 2*(pi)*k*L(T1-T2/[ln(r2/r1)]
Where Q = heatloss, k is thermal conductivity of insulator, L is pipe length, T1 & T2 are ext and internal temps, ln is natural log, and r2 & r1 are outer & inner radii of the insulation. Using 0.038 as k (for Armaflex at 40degC) & for 22mm copper with ΔT70 I get 36W loss per metre with 13mm Armaflex and still 22W with 25mm Armaflex.