Hi,
I will be replacing my old gas hob&oven with a Smeg A1P-5. As the new cooker is a gas hob with an electric oven (plug already fitted by manufacturer) a new supply will be required. The manual states the Smeg is rated at 3.0 kW (nominal power) and requires a 13Amp power supply.
With the CU approx. 5m from the kitchen, would the following radial circuit be suitable:
2.5mm T&E from 16A MCB into Cooker Switch/Socket - continuing in 2.5mm T&E to a 13A DP unswitched socket where I could plug in the Smeg.
Thanks