Baxi 24Kw Eco 80, works CH ok, Hw water at 9.8 litres a minute is 10deg short of it's heat rise, cold is comeing in at 13deg so should be 48deg, is it bolloks, it's only 38deg, the washbasin is about 300mm from the boiler so no long dead leg, 28mm gas from meter for lot of the run then 22mm so not undersized.
If I screw it down to about 6 litres a minute it will go to about 50ish deg.
and further max about 53deg.
Right, the DHW xchanger is sqweaky clean as I removed it and flushed it, no crap came out, which isn't suprising as it had X400 in for about 4 weeks and the boiler was fitted onto a new CH system so all clean anyway, the HW sensor is ok and boiler modulates, manometer burner pressure is spot on at 12.2 mb and modulates if you screw tap down slowly, rate at the meter is 23.36Kw input, the heat ISN'T going down the flow pipe as I checked from stone cold system AND turned off isolation valves to 100%prove no loss around heating, took burners out and flushed through under tap, sucked and blew dry with hoover, all clear, and checked all jets clear, so, where the F**** is the 10 degrees disappearing, or is it that Baxi are a bit "generous" with their Spec, I phoned their Tech line and told them all I had checked, and they dont know whats wrong either
Any one had a similar problem and got any ideas or am I and Baxi tech missing something dead obvious
If I screw it down to about 6 litres a minute it will go to about 50ish deg.
and further max about 53deg.
Right, the DHW xchanger is sqweaky clean as I removed it and flushed it, no crap came out, which isn't suprising as it had X400 in for about 4 weeks and the boiler was fitted onto a new CH system so all clean anyway, the HW sensor is ok and boiler modulates, manometer burner pressure is spot on at 12.2 mb and modulates if you screw tap down slowly, rate at the meter is 23.36Kw input, the heat ISN'T going down the flow pipe as I checked from stone cold system AND turned off isolation valves to 100%prove no loss around heating, took burners out and flushed through under tap, sucked and blew dry with hoover, all clear, and checked all jets clear, so, where the F**** is the 10 degrees disappearing, or is it that Baxi are a bit "generous" with their Spec, I phoned their Tech line and told them all I had checked, and they dont know whats wrong either
Any one had a similar problem and got any ideas or am I and Baxi tech missing something dead obvious