I have a solar thermal system with a Resol Delta Sol BS Plus controller. I have recently had some works done to the system and since then it does not appear to be functioning properly and I wondered if anyone had any ideas about what could be wrong.
The issue is that when the system’s pumps turn off, either because a store has reached its max temperature or because the system is checking its temperature during an Oscillating Break Time, the system (through the collector sensor) no longer detects an increase in temperature at the top of the collectors.
What happens is that the pumps turn off and the collector sensor actually registers a decrease in temperature at the top of the panels. This goes on for as long as the pumps are off and the temperature just falls steadily.
If the pumps are turned back on manually, the flow of the system start circulating again, the temperature reading at the collector sensor then rockets up by 10 – 20 degrees or more and then levels out once the pumps have taken back control, released the heat through the heat exchangers etc.
It’s an issue because it means that (a) the store prioritisation is no longer working properly and (b) the system doesn’t detect when it’s about to overheat and so doesn’t restart the pumps in an emergency fail-safe function (e.g. under the OREC or OCX functions).
It didn’t used to be a problem. On a sunny day, what used to happen is that when the pumps turned off, the collector sensor would detect a steadily rising temperature and then the system behaved as expected, heating the stores in the right priority… with the other system controller functions etc.
Has anyone ever heard of or encountered this issue?
The issue is that when the system’s pumps turn off, either because a store has reached its max temperature or because the system is checking its temperature during an Oscillating Break Time, the system (through the collector sensor) no longer detects an increase in temperature at the top of the collectors.
What happens is that the pumps turn off and the collector sensor actually registers a decrease in temperature at the top of the panels. This goes on for as long as the pumps are off and the temperature just falls steadily.
If the pumps are turned back on manually, the flow of the system start circulating again, the temperature reading at the collector sensor then rockets up by 10 – 20 degrees or more and then levels out once the pumps have taken back control, released the heat through the heat exchangers etc.
It’s an issue because it means that (a) the store prioritisation is no longer working properly and (b) the system doesn’t detect when it’s about to overheat and so doesn’t restart the pumps in an emergency fail-safe function (e.g. under the OREC or OCX functions).
It didn’t used to be a problem. On a sunny day, what used to happen is that when the pumps turned off, the collector sensor would detect a steadily rising temperature and then the system behaved as expected, heating the stores in the right priority… with the other system controller functions etc.
Has anyone ever heard of or encountered this issue?