Hi all,
Please can you throw some light on this problem ?
The background......
Thermecon W40/50 internal wall mounted. Fitted in a cupboard in an upstairs bathroom, no vents in the door or wall. Told customer that there should be some. Supposed to have been 'serviced' 4 months before I got the call that it had locked-out and was kicking out soot. Customer could not find the service paperwork.
Got there, spent most of the time de-sooting that SOB.
It was in the bathroom upstairs in a cupboard that the bottom was three feet off the floor, so spent the morning up and down steps and bent double. Covered in soot and one and a half henry bags later, I never seen so much soot. The bottom baffle lip on the combustion chamber was almost burnt through - just an inch left, the plastic air tube where the snorkel fixes was a bit melted. Nozzle in there was a 0.50x60*W, difuser to nozzel was 12mm, pump pressure 140psi.
Put a 0.45x80H in at 115psi, CO2 @ 11% - as per customers manual.
Customer said it now does not shake the house when it fires up !
Apart from the above when I went to re-fit the snorkel, the flappy bit at the end folded in and blocked off the air, so removed and made sure this was outside. As the customer said that the other service man had left it off and he refitted it, maybe when the customer refitted it blocked off most of the air ?
I left it running OK on 27th March, now a month later he rings me again to say it is just as bad as before kicking out soot.
It is supposed to be a 4yr old boiler.
Got to go back tomorrow...
Should the bottom baffle have a drop down leg that rests on the combustion chamber baffle lip?
Thanks in advance.
Please can you throw some light on this problem ?
The background......
Thermecon W40/50 internal wall mounted. Fitted in a cupboard in an upstairs bathroom, no vents in the door or wall. Told customer that there should be some. Supposed to have been 'serviced' 4 months before I got the call that it had locked-out and was kicking out soot. Customer could not find the service paperwork.
Got there, spent most of the time de-sooting that SOB.
It was in the bathroom upstairs in a cupboard that the bottom was three feet off the floor, so spent the morning up and down steps and bent double. Covered in soot and one and a half henry bags later, I never seen so much soot. The bottom baffle lip on the combustion chamber was almost burnt through - just an inch left, the plastic air tube where the snorkel fixes was a bit melted. Nozzle in there was a 0.50x60*W, difuser to nozzel was 12mm, pump pressure 140psi.
Put a 0.45x80H in at 115psi, CO2 @ 11% - as per customers manual.
Customer said it now does not shake the house when it fires up !
Apart from the above when I went to re-fit the snorkel, the flappy bit at the end folded in and blocked off the air, so removed and made sure this was outside. As the customer said that the other service man had left it off and he refitted it, maybe when the customer refitted it blocked off most of the air ?
I left it running OK on 27th March, now a month later he rings me again to say it is just as bad as before kicking out soot.
It is supposed to be a 4yr old boiler.
Got to go back tomorrow...
Should the bottom baffle have a drop down leg that rests on the combustion chamber baffle lip?
Thanks in advance.