No - your design has no overcurrent protection for the cable.Am I right in thinking all I need at the service end is an RCD and isolator straight from the service block? (as shown)
Yes. You could also swap the RCD for an MCB. Leave the isolator there. It provides double pole iso - an MCB only provides phase iso.There is overload protection on the spa end.
But I could then just swap the isolator for an mcb?
Replace the isolator & RCD with a SP & N switchfuse.Yes. You could also swap the RCD for an MCB. Leave the isolator there. It provides double pole iso - an MCB only provides phase iso.
(Although I am several years ex electrician I would have used a switchfuse)
BTW, if your spark wanted to install it this way, don't employ him. And ring his scheme provider ASAP: he is installing contrary to 7671.
433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor in the part of the run between the point where a change occurs ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfills at least one of the following conditions:
(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )