While having some building work done, a 2.5mm T&E cable was found in an inconvenient place (coming from loft to floor level) . It's on a 20A MCB circuit, which I had assumed was a radial circuit
On investigating to work out which sockets would be disconnected if that wire was removed, I found that *none* would be. Looking inside the consumer unit there are two 2.5mm wires going to the MCB
So, it looks like it's a 2.5mm ring main with a 20A MCB. Which wasn't what I expected at all. (it looks like there are another 2 circuits the same in the CU, and a 32A ring with the same size cable, for the kitchen)
(the house was completely rewired a couple of years ago, before we bought it, so I'm not sure why it was done this way - maybe the 20A MCBs were on a special at Aldi that week... )
Now, I believe it'll be fine to remove the inconvenient wire (and retest earth continuity/impedance) and convert the ring to a radial, but am I missing something?