Is it possible to split the 6mm cable 30A supply to a cooker rated at 4410W Max and an Induction Hob rated at 7kW Max?
433.2.2 is the problem regulation and it requires that where a supply is split you fit a automatic disconnection device. (Fuse)
433.2.2 The device protecting a conductor against overload may be installed along the run of that conductor in the part of the run between the point where a change occurs ( in cross-sectional area, method of installation, type of cable or conductor, or in environmental conditions ) and the position of the protective device has neither branch circuits nor outlets for connection of current-using equipment and fulfills at least one of the following conditions:
(i) It is protected against fault current in accordance with the requirements stated in Section 434
(ii) It's length does not exceed 3 m, it is installed in such a manner as to reduce the risk of fault to a minimum, and it is installed in such a manner as to reduce to a minimum the risk of fire or danger to persons ( see also Regulation 434.2.1 )
Should Andy plug the 4.4kW applance into the socket, or the 7kW one?Is it possible to split the 6mm cable 30A supply to a cooker rated at 4410W Max and an Induction Hob rated at 7kW Max?
you surely haven't been misled by the size of the push-on G&Y sleeving?...3 conductors of differing sizes?
Should Andy plug the 4.4kW applance into the socket, or the 7kW one?