Spurs off spurs

Joined
25 Nov 2006
Messages
538
Reaction score
10
Location
London
Country
United Kingdom
Hi. While I've got the floorboards up in the bedroom I've been following the cabling and wanted to check if this is correct.

There's obviously been some changes made because there's a lot of defunct cabling which I've pulled out but what is left is this:

The first double socket is a spur off the ring main. This runs to a another socket with a switched fused spur which then runs to another socket with another switched fused spur.

I don't know why there's no ring in that room but is it acceptable? Thanks.
 
Last edited:
Sponsored Links
You really need to verify first that you actually have a ring final circuit, especially if there's evidence of alterations. Ring finals aren't compulsory but they are a neat way to maximise the investment in cable required to go round a room. Radials are completely acceptable and sometimes more efficient but that depends on the routes the cables take and what load you are planning on using on the circuit.

Assuming you are actually looking at a spur from a ring final circuit then no your current setup is not acceptable-electrically it is only moderately unsafe, operationally you've got fuses protecting fuses which will always be fun when fault finding.

If you sure that you have a ring final circuit to spur from (2 bits of T & E at a socket doesn't guarantee a ring) you need to insert a fused connection unit between the ring and the first spurred double socket (ideally the FCU would be in the ring rather than on the spur cable). You can then junk the subsequent FCUs (unless they're feeding something else as well as the socket) and hang as many sockets on the spur as you like since the cabling is all being protected by the first FCU.
 
Thanks.

Assuming (and I take your point on not making assumptions) it is a spur off the ring final circuit, if the first socket had an FCU would it make it safer or legal? It's surface mounted and could be swapped for a single socket and FCU. Thanks.
 
Assuming it is a ring final on 2.5mm cable then 7.2.2 of the On Site Guide says you can have an unlimited number of socket outlets fed from a fused spur (max rating of fuse in the spur dependent on spur cable size and 13A in any case). Your plan will make your setup safer and compliant (ring-FCU-millions of sockets)
 
Sponsored Links
Just remembering that the total maximum load for all of the additional sockets will be 13A as that is the largest fuse that the FCU will allow.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top