Hi,

Just looking for any wisdom out there before I start.
100k twin burner Stanley fitted with Monoflame burners, Danfoss pump etc.
I put the heating on the other night, ran for maybe 45 minutes, then it tripped the house earth leakage trip.
I reset it and 10 minutes later the Stanley went through it's start up motions again, and out went the trip again.
I turned it all off

The rest of the system would be on, pump, valves etc but I think that fact the Stanley was about to start is significant.
Just wondering if anyone has been there, done that etc.

Thanks

Andy
 
Sponsored Links
Solenoid for sure. Not tripping with it unplugged, just going to lockout.
Boiler now running with solenoid coil off the cooker burner.

A
 