I'm in the process of laying a concrete floor that requires 100mm of concrete with a layer of a142 mesh

Due to the location i will have to cut the mesh in order to get it into place.

my question is this - what is the minimum overlap necessary to retain the strength

thanks

tim
 
Sponsored Links
t1mgreen said:
I'm in the process of laying a concrete floor that requires 100mm of concrete with a layer of a142 mesh

Due to the location i will have to cut the mesh in order to get it into place.

my question is this - what is the minimum overlap necessary to retain the strength

thanks

tim

Two squares is plenty, lap required for A142 (6mmDIA in 20N conc) is about 260mm from memory.
 