Can anybody tell me approx what reading I should get across the element (ohms) using a multimeter or are these better tested using a meggar. (If thats how you spell it)
PR=V^2
R=V^2/P
however if you have multiple elements in your heater
R=V^2/(P/N) where R is the resistance of an element P is the power rating of your heater V is the voltage rating of your heater and N is the number of elements in the heater
The readings were 66ohms +/-0.4 over the 3 elements.
Problem was the heater was not very hot when at the usual setting, so I have swapped thermostats with another heater and after a 1 hr boost the fault would appear to be in the other heater now. So new thermostat needed me thinks.
Close, it's Megger (name of one of the most common testers).
You use a standard meter to measure resistance. However, if you want to test the insulation of something- for example the impedance to earth (should be a very high reading) then you use a Megger.
The reason is that the megger puts about 500v across the item under test in order to stress it. That's why you have to be careful where you use them. There are many who have made the mistake of meggering a piece of electronics and then wondering why it doesn't work any more.