strange end to end continuity ring main readings
28 Oct 2003
Staffordshire
can anyone help to interpret these ring main readings
end to end tests
L-L 0.46
N-N 0.45
E- E 0.30
The ring is wired in 2.5 mm twin + earth 1.5mm cpc so reading on cpc continuity should be higher dont know why this is .
further tests
x-link L - N 0.23 0.23 0.23 0.23 0.24 0.25 0.22 0.24
x-link L - E 0.26 0.28 0.18 0.27 0.28 0.26 0.21 0.30
i have had socket fronts off to ensure good contact and checked connections.
would these readings be ok to sign off
thanks
Is it included in supplementary bonding? Dual box used for 2 accessories on different legs of the ring?
FIrst time I found that sort of "odd" reading was : -
First socket on one leg was in a bedroom with a bond to the taps of the wash-basin. First item on the other leg was the FCU to the boiler. Various 15 mm copper pipes parallel to the CPC.