Morning everyone,
Got an usual install and weird things happening in the bathroom.
Immersion heater is switched via a contactor by the GSHP controller, which is about 30m away in an outbuilding. Contactor is in a box in the airing cupboard near the tank. Immer can also be switched by a another contactor (in the same enclosure) which is switched by a Horstman Electrisave (this setup was recommended here by Coljack IIRC).
Occasionally, a contactor can be heard to close unexpectedly. On one occasion, I've actually been in the bathroom and seen the visual indicator on the GSHP switched one showing closed. The GSHP controller shouldn't be calling for heat (it only does this once a week in the middle of the night to pastuerize the tank; this works correctly).
I've swapped the contactor with another, and the problem remains on the immer cct. Isolating the immer supply doesn't stop the contactor closing either.
The thing is, after many months I've realized that this only seems to happen in the morning. It coincides with the period that the UFH is on. The cable that supplies the UFH controller (Aube TH132) runs alongside the contactor cable for about 2m. Both are 6242Y, in 2.5 & 1.5. They are buried in the wall, which is now tiled, so are not easily accessible.
Is it possible that the UFH is inducing sufficient voltage in the contactor cable to close it ? Any suggestions on suitable datalogger (and where I can hire one) to prove or disprove my suspicions ?
If the worst is true, is there a remedy which does not involve replacing or rerouting cables ?
Thanks, David
Got an usual install and weird things happening in the bathroom.
Immersion heater is switched via a contactor by the GSHP controller, which is about 30m away in an outbuilding. Contactor is in a box in the airing cupboard near the tank. Immer can also be switched by a another contactor (in the same enclosure) which is switched by a Horstman Electrisave (this setup was recommended here by Coljack IIRC).
Occasionally, a contactor can be heard to close unexpectedly. On one occasion, I've actually been in the bathroom and seen the visual indicator on the GSHP switched one showing closed. The GSHP controller shouldn't be calling for heat (it only does this once a week in the middle of the night to pastuerize the tank; this works correctly).
I've swapped the contactor with another, and the problem remains on the immer cct. Isolating the immer supply doesn't stop the contactor closing either.
The thing is, after many months I've realized that this only seems to happen in the morning. It coincides with the period that the UFH is on. The cable that supplies the UFH controller (Aube TH132) runs alongside the contactor cable for about 2m. Both are 6242Y, in 2.5 & 1.5. They are buried in the wall, which is now tiled, so are not easily accessible.
Is it possible that the UFH is inducing sufficient voltage in the contactor cable to close it ? Any suggestions on suitable datalogger (and where I can hire one) to prove or disprove my suspicions ?
If the worst is true, is there a remedy which does not involve replacing or rerouting cables ?
Thanks, David