This has just started happening and seems intermittent.
Potterton Boiler and controller
Siemens 3 port diverter valve MA-V322C
Problem is that the heating will sometimes turn on even when the thermostat is set below the room temperature. The only way to cure this is to switch off the AC supply to the controller. If the controller is changed the fault persists.
Switch on Central heating on controller,
Turn thermostat above room temperature, valve moves to CH and boiler starts
Turn thermostat off, valve remains in CH position
Turn CH off at controller, valve remains in CH position
Turn off at ac supply to controller and valve returns to HW position